The 3051 displays garbled characters; are all the characters fully lit?

2019-02-26View Original

Thread Content

This post was last edited by Electronic cabbage on 2019-2-26 at 18:40. The 3051 pressure transmitter shows garbled characters on its screen; all the characters appear fully lit. Experts, what could be the problem?
Reply #22019-02-26
Is the loop current correct? It’s possible it’s just a problem with the display module
Reply #32019-02-26
Hello, the loop current is incorrect; it always stays at a maximum of 20mA.
Reply #42019-02-26
Is it probably a motherboard issue? I’ll have to try with a different motherboard; it seems I’ve never seen any issues with the power supply modules of this model other than overvoltage or water damage
Reply #52019-02-26
It’s a question no one knows the answer to. . . You are the one who found the person in charge of developing the instrument; explain it to him, and even then it will be difficult for him to determine where the fault lies. Take it back to the factory for repairs. :lol.
Reply #62019-02-27
Take the modules from other transmitters and try them out, using the elimination method. Anyway, these transmitters are modular, making them easy to disassemble
Reply #72019-02-27
This situation is usually caused by a motherboard failure; you can try turning off the power and restarting it, but if that doesn’t work, the motherboard will need to be replaced.
Reply #82019-02-27
The motherboard is faulty; it’s better to send it to the factory for repair since it’s not even within the warranty period~
Reply #92019-03-04
It might be that the power connection is loose; try reconnecting the power cable. Or try a different power supply. Anyway, there are only two possible explanations for this issue: either there is a problem with the power supply, such as an improper connection or instability… or there is an improper connection or malfunction in the hardware of the instrument

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.