Need help with Rosemount sensor wiring!

2019-08-01View Original

Thread Content

The previous image shows the wires of the temperature transmitter sensor that need to be replaced; there are six wires in total: two red, two blue, one black, and one white. The image below shows the gauge that needs to be replaced now, and it is a four-wire system. Could someone please advise me on how to connect these wires? I need to use the six-wire sensor with this four-wire gauge. Thank you very much! ????????
Reply #22019-08-01
This post was last edited by tiger2010 on 2019-8-1 at 19:08; the image shows its wiring instructions
Reply #32019-08-01
Could you specify the color code? I have no foundation; I simply can’t understand this. Should red, blue, black, and white be connected to those wires numbered 1, 2, 3, 4, and 5 in a 4-wire system?
Reply #42019-08-02
This post was last edited by tiger2010 on 2019-8-2 07:52. Is the sensor with 6 wires not usable? Can you be sure that the black/brown/blue wires on the left form one set of sensors?
Reply #52019-08-02
The first image shows a Rosemount integrated temperature transmitter. Those thin lines in the image represent the thermal resistors inside the transmitter; they are not related to the wiring. Usually, a wiring diagram is indicated on the back cover of the transmitter. To replace the transmitter, simply connect the control signals to the 4-20mA output, and that’s it
Reply #62019-08-03
Are you trying to connect six wires to a transmitter with four wires? If so, the first step is to divide them into groups: one red and black group, and one blue and white group. Only three wires from one of these two groups can be used for wiring.
Reply #72019-08-03
It is best to use a handheld device to change the instrument configuration to a three-wire system; after making this change, connect 1 to black and 2 and 3 to red. Either 1 connects to white, and 2.3 connect to blue.
Reply #82019-08-03
If it is not changed to a three-wire system and is still connected in a four-wire manner, connect the wires of the same color to 1 and 2, connect the remaining wire to 3, and then use a jumper wire to connect 3 and 4. It is recommended to change the instrument to a 3-wire system.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.