Seeking Modbus communication for Ingersoll Rand centrifugal air compressors

2019-12-07View Original

Thread Content

The first image shows the compressor model, the second image shows the appearance of the control cabinet, and the third image shows the communication module
Reply #22019-12-08
Thank you, I’ve figured it out: the baud rate is 9600, there are 8 data bits, 1 stop bit, no parity check, the address is 16. It’s a two-wire connection with RX+ and RX-, where TX+ is connected to RX+ and TX- is connected to RX-. However, there is packet loss in the data, measured directly at the terminals inside the compressor control cabinet

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.