HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Help: What is the maximum distance between the cabinet room and the control room?

2020-03-06View Original

Thread Content

Maximum distance between cabinet rooms and control rooms
Reply #22020-03-06
The control system uses optical fiber connections for communication and control between the cabinet rooms and the control room. Theoretically, the maximum distance depends on the distance limitations between the fiber optic cable and the switch. Single-mode fiber can theoretically transmit over dozens of kilometers, so it should be able to meet ordinary distance requirements.
Reply #32020-03-06
There’s another question: if the control room is currently in the same building as the cabinet room, and the main power distribution room is also located in that same building, and now we want to move the control room to another building while keeping the cabinet room in its current location, is this in compliance with the regulations? Please help, thank you
Reply #42020-03-06
1. This is likely an old installation, with the power transformation and distribution area as well as the control room in one place (SH-3006-2012), which is non-compliant; 2. It should be feasible to move the control room to another building; it is recommended to engage a reputable design firm for the design work. 3. I estimate that the current safety distance required by GB50984-2014 for the control room in terms of overall layout is not sufficient. Moving it aside can also solve this problem.
Reply #52020-03-06
Can you add me on VX 18931155795? Thanks
Reply #62020-03-07
I see that the specifications don’t state that the cabinet room cannot be located together with the power distribution room, right?
Reply #72020-03-07
In terms of the cabinet room, I don’t see any regulation stating that it cannot be located together with the power distribution room, right? This approach does not comply with the regulations, and there are many factors to consider, such as electrical interference issues, safety distances, and management aspects, among others

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.