Regarding the grounding issue of the interlock wires with electricity

2020-12-11View Original

Thread Content

Interlocking of motor start/stop, and the operating status of the motor. At which end should the shield wire of the interlock cable between the instrument cabinet room and the electrical distribution room be grounded?
Reply #22020-12-11
We have received a request to implement single-sided grounding for the instrument cabinet
Reply #32020-12-12
Between the electrical and instrumentation disciplines, the signal connection cables are grounded on the instrumentation side, while the power connections are grounded on the electrical side.
Reply #42020-12-21
It depends on the situation. In all the projects I’ve worked on, there is a dedicated instrument and electrical transfer cabinet in the electrical distribution room; the electrical side is grounded electrically, while the instrument side is grounded indirectly through the instrument cabinets. In short, it should still be single-point grounding. If it doesn’t go through the instrument and electrical transfer cabinet, I have a personal suggestion: for the interaction between electrical and instrument signals, there is definitely a dry contact side and a power supply side; it might be advisable to ground the side that supplies power to the signals. In other words, if power is supplied from the electrical side, it is grounded on the electrical side; if power is supplied from the instrument side, it is grounded on the instrument side. Of course, this is a bit troublesome; grounding it to either side directly isn’t a big issue. Nowadays, grounding grid designs are used, so the probability of problems occurring with grounding is extremely low.
Reply #52020-12-21
What was said upstairs is correct; single-ended grounding is the proper solution
Reply #62020-12-21
Catch a big shot alive. For signal lines, no matter how they are connected, it’s sufficient to connect them to the ground at a single point; this is the correct way to do it. A type of two-terminal grounding that I only learned about recently is when the shielding layer of an armored cable is connected at both ends, for lightning protection purposes.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.