2022-03-04View Original

Thread Content

What are the required lengths for the outer protective sleeve and the insertion depth according to the temperature transmitter data sheet? Why is the length of the outer protective sleeve at some pipe ends zero? Is there no sleeve there? Seek answers from experts in instrument control. The person from the equipment department was completely confused :(. It would be great to have a simple diagram, thank you!
Reply #22022-03-04
For sizes below DN80, the regulations require that the pipe diameter be increased – at least to DN80. Then, adding a flange neck of 150 mm results in a total diameter of 230 mm; you should insert at least 2/3 of this length. Some larger companies require the diameter to be increased to DN100. Then add a flanged neck, along with insulation and heating
Reply #32022-03-04
Can it be understood that H is the length of the outer protective sleeve, and l is the insertion depth?
Reply #42022-03-04
First, where is this watch from? It makes my head spin
Reply #52022-03-04
Sinopec, temperature transmitter data sheet
Reply #62022-03-04
Find the person in the table to verify. In the figure below: U: Usually the data provided by the process (insertion depth) ; L, l: These are the data for ordering the gauge (l is the insertion depth) ; H, U: Data from equipment manufacturing (U is not always present)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.