Are the DI cards of PLCs/DCSs by default passive contacts for input?

2023-10-10View Original

Thread Content

Are the DI cards of PLCs/DCSs by default passive contacts for input? There’s no need to connect an external 24V power supply, right?
Reply #22023-10-10
The DI cards of both PLCs and DCSs use passive contacts as the default input. This means they can receive external switch signals and convert them into digital signals for processing, without the need to connect an external 24V power supply. .
Reply #32023-10-11
The DI cards of DCS are generally set to passive input by default; no external 24VDC supply is required, as the DI cards themselves provide the 24VDC power for the DI circuits. Some DI inputs of the PLC require an additional 24VDC supply.
Reply #42023-10-11
Not necessarily; there are also active signals!
Reply #52023-10-12
I would like to ask under what circumstances an active signal appears
Reply #62023-10-13
The signals of the DI module can be active or passive; they can be connected to the corresponding terminals of the module as needed. As for whether they are active or passive, that isn’t important

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.