Why is there no output from the FC105 module in step7?

2025-03-15View Original

Thread Content

I’m a complete beginner. I’ve tried to create several flow meters by following others’ examples; the signal from these meters is 4-20mA, and the hardware settings are correct, but there’s no output. As shown in the image below, I would be extremely grateful if someone could give me some advice
Reply #22025-03-16
In the programming interface, it can be found under \"Program Elements\" → \"Libraries\" → \"Standard Library\" → \"TI-S7 Converting Blocks\". Note: Do not use FC105 and FC106, which are located under \"S5-S7 Converting Blocks\"; these functions are intended for S5 input/output templates and cannot be used with S7 input/output templates.
Reply #32025-03-16
Thank you, boss. I was wondering why there was no output, and after changing the range, when I reopened the program, the range reverted to its default value again. 😳

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.