What are the design requirements for the slope of steam pipes?

2015-06-08View Original

Thread Content

Are there any requirements for the slope of steam pipes? If it is sloped toward the boiler or toward the point where steam is used, at what distance should a drain valve be installed, and at what distance should a U-shaped pipe be used for compensation?
Reply #22015-06-10
Horizontally installed pipes should have an appropriate slope; when the slope is in the same direction as the steam flow, a slope of i=0.003 should be used, while when it is in the opposite direction to the steam flow, the slope should be increased to i=0.005–0.01. Traps should be installed at the turns and at the ends of the main pipes
Reply #32015-06-25
The slope should preferably be in the direction of the air flow. Shape compensation is aimed at the thermal expansion of pipes, which is not hydrophobic. In horizontal pipes where there is no lowest point, a drain point must be added every 150 meters of length.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.