2015-06-16View Original

Thread Content

Regarding pulse accumulation, how does the system collect, calculate, and output it to the monitoring system? I want to determine how to set the range of a mass flow meter.
Reply #22015-06-16
Flowmeters like this generally have a 4-20mA signal output, which is connected to the AI card of the DCS. If pulse signals are to be acquired, a dedicated pulse card is required, which is rather troublesome. Aren’t parameters such as range indicated on the instrument’s nameplate? Alternatively, the range options are also available in the instrument settings; if you’re really unsure, consult the manufacturer.
Reply #32015-06-16
If it is a pulse signal, then a pulse input card is required, or else a pulse transmitter can be used; in other words, the standard current signal is generated based on the number of pulses

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.