What size circuit breakers and cables?

2015-06-17View Original

Thread Content

Hello everyone, I have a steamer for making mantou here, with a power rating of 24KW and it operates on 380V three-phase electricity. What size circuit breaker and aluminum cable should be used? Currently, using a 60A circuit breaker and 10MM2 aluminum cable causes overheating. The circuit breakers are from Chint, and 6 of them have already been replaced due to burning out. How can I avoid burning it out? Thank you all!
Reply #22015-06-18
To achieve both savings and safety. It’s best to use a 60A circuit breaker with a leakage protection function; it’s a heater, not a motor, right? It’s the three-phase star connection. Multiple strands of soft wire with a cross-sectional area of 10 m² (copper) are covered with copper connectors on the terminal posts to enhance the skin effect; these wires are also connected using copper-aluminum connectors and fixed in a junction box mounted on the wall. Copper connectors should be installed at both the source and the load end. Add a ground to the enclosure.
Reply #32015-06-19
Since the steamed bun maker is a pure resistive load, the current I is equal to power P divided by voltage V: 24000/380 = 63.16 A. Therefore, the minimum rating for a circuit breaker should be 80A or 100A. The cable should use a copper core with a cross-sectional area of 16 square millimeters ; For the aluminum core, 25 square millimeters is a suitable choice. As mentioned above, it’s best to choose a circuit breaker with leakage protection. The exterior of the steamed bun maker must be grounded. It’s necessary!
Reply #42015-06-21
Sit down and learn *electrical knowledge – steamed bun maker – pure resistive load.
Reply #52015-06-21
Choose an air circuit breaker of 80A, and select a copper-core cable with a cross-sectional area of 16 square millimeters
Reply #62015-06-24
Everyone’s discussions have been very helpful to me; thank you all here. :):):):):)
Reply #72015-06-27
For a three-phase load, this way of calculating the current is incorrect, right? I = P/380/1.732/power factor; the power factor for a resistive load should be 1. Therefore, the current is 36.45 A, so a 60A circuit breaker is suitable! Additionally, when using three-core copper wires of types RV or BVV, at an ambient temperature of 30 degrees, a current of 48A is permissible for 10mm2 wires; therefore, a 10MM2 copper wire is sufficient
Reply #82015-06-27
When it’s in operation, buy a clamp ammeter to measure the current; that way you’ll know. Electricians also need this type of meter!
Reply #92015-06-28
You’re right; I missed one square root of 3. Thanks for the reminder.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.