First, it is necessary to convey flue gas at a temperature of 200 degrees and a density of 0.75, in a volume of 12,700, with a total air pressure of 120 mmH2O. There is one fan whose nameplate specifies a flow rate of 12,700 and an air pressure of 160 mmH2O; it is necessary to verify whether this fan is suitable for use.
Reply #22015-09-17
One fan has a nameplate flow rate of 12,700, and a wind pressure of 160 mmH2O; it has been verified to be usable
Reply #32015-09-17
The selection of a fan is related to the medium and temperature! Just looking at pressure and flow rate is sufficient for use
Reply #42015-09-17
This question is so specialized; as a layperson, I don’t understand it. Please explain
Reply #52015-09-17
It cannot be used; the flow rate indicated on the nameplate is the flow rate under standard conditions.
Reply #62015-09-17
【Solution】According to the given conditions, the total wind pressure of the system under experimental conditions is 192 mmH2O, which is greater than 160 mmH2O; therefore, this fan is not usable.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.