Can a pressure transmitter with a range of 60 kPa be used in place of a pressure transmitter with a range of 1.0 MPa? We are now preparing to upgrade our old sensors, and the spare parts available are pressure transmitters with a range of 1.0 MPa; in actual use, a maximum pressure of 60 kPa is sufficient. .
Reply #22015-09-21
10/0.6=16.7 times. It’s a problem related to measurement accuracy; generally speaking, it’s not very suitable.
Reply #32015-09-21
It depends on the accuracy of your transmitter; generally, better transmitters have a range ratio of up to 10. I’m not sure what the value is for your transmitter
Reply #42015-09-21
It’s not quite appropriate. It can be used, but the accuracy will be much lower
Reply #52015-09-21
I want to ask this question too. Is there an answer?
Reply #62015-09-21
It also depends on the measurement range of the sensor in your pressure transmitter; if it’s within that range, it can be used as long as the values aren’t too close to each other But the accuracy might be a bit worse than before; if it’s within that range, it’s completely unusable, as this could damage the pressure sensor!
Reply #72015-09-22
It works fine; there’s no problem, just the accuracy is a bit lower. In fact, the accuracy of pressure transmitters is already very high; in the petrochemical industry, an accuracy of 0.2% is sufficient for pressure transmitters.
Reply #82015-09-22
It depends on what the minimum range of your pressure transmitter is. If the minimum range can be set to 100 kPa, then there will be no problem.
Reply #92015-09-22
Check the linearity ratio of the pressure transmitter; a good one can be used. Of course, the premise is that the required precision for 60 KPa doesn’t need to be too high
Reply #102015-09-22
It’s better to buy a new one,,,
Reply #112015-09-22
The range of 0~60 KPa should be set manually using the controller

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.