There is a system that communicates with the DCS using MODBUS; the DCS is a JX-300XP central control system. The issue is as follows: The data sent by the other system comes in two-byte and four-byte formats. Two-byte data is processed normally, but four-byte data cannot be parsed correctly. The problem is now pretty clear: the register address provided by the other party refers to a 32-bit, four-byte variable, but DCS cannot directly read four-byte variables. What are the possible solutions?
Reply #22015-11-18
For 32 bits, it should be a real number; currently, it is converted to a 16-bit integer in the other system, and then converted back here at the control center.
Reply #32015-11-18
The Modbus protocol does not specify a 32-bit data type; it only defines 16-bit register data. Therefore, programming is required to address this issue, whether on the slave side or the master side – in any case, one must take action to handle this data type problem
Reply #42015-11-21
It’s very likely that the high 16 bits and low 16 bits of the word are reversed; the floating-point value can be converted to a 16-bit integer on the slave side, or the high 16 bits and low 16 bits can be swapped on the master side
Reply #52015-11-23
Use Modbus scan to determine the data type; it might be a 64-bit double type. In some systems, the cumulative values are indeed of this double type – for example, the cumulative values in Daniel flow meters are of this data type. Floating-point numbers generally consist of 4 bytes, and the possible ordering patterns are 1234/3412/2143/4321 and similar. . . . Feeling nauseous is especially bad in such situations. . . . For Siemens PLCs, when using a Modbus communication adapter, the floating-point format is 3412, while the regular format is 1234
Reply #62015-11-24
Check the DCS manual to see how data types are defined; some are called real, while others are called dword
Reply #72015-11-26
The original poster and other forum members have used the MODBUS protocol. For the MODBUS_RTU protocol, it is possible to transmit n data points at a time – what is the maximum value for this n? That is, how many data points can MODBUS_RTU transmit at most each time? n can’t be infinite; otherwise, the data transmission would never end.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.