The Rosemount 3501 differential pressure transmitter suddenly reached full scale

2015-11-29View Original

Thread Content

I’m currently using a Rosemount 3501 differential pressure transmitter. This afternoon, it suddenly reached its full scale reading. After turning off the power at the site and then turning it back on, the reading returned to normal. What caused the transmitter to reach its full scale so suddenly?
Reply #22015-11-29
The medium being measured is liquefied natural gas
Reply #32015-11-29
This has happened twice already; once the power is restored, the measurement values jump to full scale instantly. Do you mean that the program inside the transmitter is running abnormally, in a loop, or that it’s caused by some interference?
Reply #42015-11-29
The full scale is 20mA; the output board of the meter is damaged
Reply #52015-11-30
The possibility of interference is high; resetting by powering on again is equivalent to an action to eliminate interference....

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.