Metso positioner calibration

2016-07-05View Original

Thread Content

Why can’t I adjust the Metso locator? Currently, the display only shows MAN CAL and 1PT CAL; all other adjustment parameters are missing (such as AUTO CAL, LCAL 3P, LCAL 9P). Could someone with expertise please give some advice!
Reply #22016-07-05
What specific model is it on site? It would be best to post the thread in the on-site instrumentation section.
Reply #32018-10-17
When the valve type is set to linear, the AUTO automatic check is hidden. If you want to use automatic testing, you first need to set the valve type to ROT, then turn off the signal and rewire it; after that, go back to the configuration settings and select linear mode – once that’s done, AUTO will be available
Reply #42018-10-18
Metso positioners are used very rarely, and they are also seen infrequently

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.