Questions regarding the replacement of cards in Siemens S7-300

2016-03-01View Original

Thread Content

Currently, when the DO card of the S7-300 outputs a signal, two DO signals are sent out simultaneously. The program has been checked and appears to be fine; it is now suspected that there is a problem with the D0 card. I would like to try using another card to see if the issue persists. May I ask whether it is necessary to disconnect the PLC’s 24V power supply when replacing the card? Also, does it need to be done for the expansion modules as well? Thank you!
Reply #22016-03-01
Checking the card isn’t that complicated, right? Disconnect the load at the output terminal and connect a multimeter; transistors operate at 24V, while relays operate at 220V. If the multimeter can detect the corresponding voltage when a signal is output, then there’s no problem with the card. . . .
Reply #32016-03-01
Currently, one relay is outputting, and the other relay will also output; when checking the program, only one relay is showing output.
Reply #42016-03-01
These two points should be in a group, connected together, so. . . Try another one
Reply #52016-03-01
Through the removal procedure, these two addresses can be tested separately to determine if there are any issues. Simply remove the front wiring harness and replace the clip

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.