Issues with running WinCC screens on virtual machines

2016-05-12View Original

Thread Content

This post was last edited by Wang Tianze on 2016-5-12 at 21:16. PCS7 is run in a virtual machine for programming and configuration, with PLCSIM used for simulation tests. Why doesn’t the display change when WinCC is used? The simulation values are set through PLCSIM, and changes can be seen in the program via simulation, but they are not visible in WinCC. I seek advice from experts! !
Reply #22016-05-12
The last edit to this post was made by Sichuan Instrument Control Beginner on 2016-5-12 at 21:51. By default, PCS7 uses named connections to communicate with the PLC via WinCC, but PCS7 does not support simulation using named connections. I’m not sure whether the latest version of PCS7 supports this feature. It is recommended that you change the connection method to TCP/IP in the OS compilation wizard of Simatic Manager, then recompile it. If the logical functions work properly during simulation tests, you can try changing it back to a named connection for actual use.
Reply #32016-05-12
Oh, when I hover my mouse over the naming link in WinCC, it keeps indicating that it’s not connected to the PLC. . . I’ll give TCP/IP a try

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.