Issues with explosion-proof hoses

2016-05-18View Original

Thread Content

Dear experts: I need help. The company has four workshops that are classified as Class A explosion-proof workshops. Most of the power cables for the electrical equipment in these workshops come from cable trays, and previously those cables were enclosed in galvanized pipes. Now a supplier claims that it’s unnecessary to use explosion-proof hoses, arguing that it’s just a waste of money. Is there any explicit regulation requiring the use of such hoses? Most of the company’s equipment is flame-retardant; the inlet points are sealed with flame-resistant material. Is it feasible to use non-flame-resistant hoses or galvanized pipes instead?
Reply #22016-05-18
Using galvanized pipes gives a neater appearance. If indoors, I prefer not to use explosion-proof hoses; cable sealing connectors for the electrical cables provide better sealing performance than explosion-proof hoses.
Reply #32016-05-18
As long as you can ensure a seal from the cable tray to the equipment connection point, it’s fine without using explosion-proof hoses.
Reply #42016-05-18
Previously, our company used explosion-proof hoses to connect the equipment directly, and the sealing performance was certainly poor. Now we are aware of this issue; for devices that are purely flame-retardant, explosion-proof connectors must be used to link the explosion-proof hoses to the equipment. If the wires are exposed directly, isn’t that harmful to them? Our company uses a large amount of organic solvents.
Reply #52016-05-18
Check: Code for Design of Electrical Installations in Explosive and Flammable Environments (GB50058-2014)
Reply #62016-05-18
Galvanized pipes are fine; for the connection points where transitions occur, explosion-proof flexible pipes can be used :)
Reply #72016-05-21
The cable tray itself is not sealed; it’s sufficient to ensure sealing at the points where it connects to the equipment. Sealing at the connections to the cable tray seems unnecessary.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.