Selection of cable trays for Class A explosion-proof workshops

2016-05-18View Original

Thread Content

Previously, steel cable trays with a cover plate on top and a bottom plate at the bottom were used. Since the workshop is an open-type facility, water easily enters the cable trays when it rains. As the cable trays have a bottom plate, the accumulated water cannot be drained promptly, which over time leads to severe corrosion of the cable trays. Now we want to replace the cable tray; I’m not sure whether a steel cable tray without a bottom plate can be used. I need a solution, thank you!
Reply #22016-05-20
I did a search – is a grid-type cable tray one that doesn’t have upper or lower covers, but only has grids to support the cables?
Reply #32016-05-21
Previously, steel cable trays with a cover plate on top and a bottom plate at the bottom were used. Then you are using trough-type steel cable trays; you can also use tray-type, stepped, or modular cable trays.
Reply #42016-05-23
Put simply, it’s like the basket in front of a bicycle; the cables inside are all tied up. If a cover is needed, it can be ordered from the manufacturer, which makes maintenance and inspection much easier, as there’s no need to lift the tray cover every time
Reply #52016-05-24
It’s a ladder-type cable tray; it’s not an instrument wire, so there should be no problem.
Reply #62016-05-25
Generally, such locations use trough boxes with small holes at the bottom.
Reply #72016-05-25
Those with a bottom plate are slot-type cable trays; they tend to accumulate water, and aluminum alloy can be used as the material. Or switch to a ladder-type cable tray. As long as the protective tube at the cable outlet is sealed properly with explosion-proof putty, there will be no problems; cable trays are not related to the issue of being explosion-proof or not.
Reply #82016-05-25
Do you all use protective tubes? Have you ever used direct Goran head sealing without using explosion-proof putty?
Reply #92016-05-25
You are referring to the situation where the cable enters the control column or junction box; if an explosion-proof flexible hose is not used, it can be sealed using a Golan connector, also known as a cable clamp sealing joint

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.