Setting of the alarm threshold for carbon disulfide gas detectors

2016-07-19View Original

Thread Content

This post was last edited by Pseudo Xiao Bao on 2016-9-23 at 14:14. The alarm threshold for combustible gases is generally set at 20–25% LEL; therefore, the low alarm setting for combustible gas detectors is set at 25% LEL, while the high alarm setting is set at 50% LEL. The concentration of toxic gases is less than or equal to 100% of the maximum allowable concentration or the permissible concentration for short-term exposure. Carbon disulfide: Lower explosive limit (by volume): 1.0. Control measures for exposure/individual protection: Maximum allowable concentration: 10 mg/m3. Molecular weight: 76.14. Immediate harmful concentration IDLH: mg/m3; ppm: 500. 1 ppm = mg/m3 = 3.16. IDLH at 20°C: 1580. Olfactory threshold: 0.096 ppm. MAC (mg/m3): 10 (picograms). Is this setting for the toxic gas alarm values correct? Could the experts please provide the correct setting parameters? Thank you. Measurement range: 0–150 ppm. First-level alarm value: 3 ppm (approximately 10 mg/m3). Second-level alarm values: 15 ppm (47.4 mg/m3), or 30 ppm (95 mg/m3), or 50 ppm (or……)
Reply #22016-07-19
Basis: Design Code for Detection and Alarm of Flammable and Toxic Gases in Petrochemical Enterprises (GB50493-2009), 5 Detection and Alarm Systems for Flammable and Toxic Gases, 5.3.1 Indicating and alarm devices shall have the following basic functions: 3 Measurement range for flammable gases: 0~100% of the lower explosive limit; 4 The measurement range for toxic gases should be 0~300% of the maximum allowable concentration, or 0~300% of the short-term allowable exposure concentration ; When the measurement range of the existing detectors cannot meet the above requirements, the measurement range for toxic gases can be 0~30% of the immediate harmful concentration ; 5.3.3 The alarm set values shall be determined in accordance with the following provisions: 1 The first-level alarm set value for combustible gases shall be less than or equal to 25% of the lower explosive limit ; 2 The secondary alarm setting value for combustible gases is less than or equal to 50% of the lower explosive limit ; 3 The alarm setting value for toxic gases should be less than or equal to 100% of the maximum allowable concentration/short-term allowable exposure concentration; when it is difficult to prepare standard gases for testing, the alarm setting value can be below 200% of the maximum allowable concentration/short-term allowable exposure concentration. When the measurement range of the existing detectors cannot meet the above requirements, the measurement range for toxic gases can be 0~30% of the immediate harmful concentration ; The secondary alarm setting for toxic gases shall not exceed 10% of the immediate lethal concentration.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.