Dear experts, I have a temperature transmitter that functions normally most of the time, but occasionally its reading suddenly jumps to around 80%, before returning to normal. This happens several times a day – what could be causing this?
Reply #22016-08-15
It could be interference, or it could be unstable performance of the transmitter....
Reply #32016-08-15
It is unstable; please consult a professional for specific details!
Reply #42016-08-15
You can disconnect this temperature sensor, provide it with several standard signals, and see its output. When there are sudden changes, ask the process team whether any relevant operations were carried out on site at that time. Find a approach and work through it step by step.
Reply #52016-08-15
Change to another one; there’s no other way.
Reply #62016-08-15
There is a high possibility of interference; this can also occur if the wiring is poor or if the pipes vibrate. It’s possible to check for such issues
Reply #72016-08-16
Step 1: First, check whether the wiring is secure, whether the cable insulation is in good condition, and whether the shielding wiring is proper. Step 2: If Step 1 confirms there are no issues, then replace the temperature sensor; if fluctuations still occur, it’s likely due to interference.
Reply #82016-08-17
When a fault occurs, first determine whether the problem lies with the sensor, the temperature change mechanism, or the display section; in other words, the entire circuit needs to be checked. If it is confirmed that the temperature change mechanism is damaged, replace it directly
Reply #92016-08-18
Our two on-site level gauges are located 100 meters away from the central control PLC; the signal wires lack a shielding layer, which causes the readings to be unstable frequently. Will installing your protective tube work in this situation?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.