Layout of fire alarm detectors in the power distribution room

2016-08-24View Original

Thread Content

Is it mandatory to install both smoke detectors and heat detectors in the distribution room? Which standard does it come from?
Reply #22016-08-24
It is mandatory; Article 11.5.21 of the standard \"GB 50229-2006 Code for Fire Protection Design of Thermal Power Plants and Substations\" sets clear requirements in this regard

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.