2016-12-02View Original

Thread Content

The medium is butyraldehyde; the flow meter is installed vertically, and it features a separate electronic system. The problem is that during operation, the flow meter suddenly returns to zero reading. Moving the extension cable restores normal operation, or sometimes it returns to normal on its own without any intervention. What could be the issue?:):):)
Reply #22016-12-02
As the original poster said, it is advisable to focus on checking whether the various signal cables are loose. Since the flow meter is installed on a vertical pipe, it is also necessary to check whether there is any vibration in the pipe.
Reply #32016-12-02
Pay special attention to checking whether the signal wires are loose. Also, determine how long it takes for the signal to return to zero; if this issue is only temporary, check the shielding and grounding of the signal wires, and ensure that all operational factors have been ruled out Check the vibration of the pipeline
Reply #42016-12-02
Butyraldehyde is definitely a liquid, and when using a vortex flow meter to measure liquids, it is necessary to have a full pipe and stable flow; therefore, the flow meter should be installed in a horizontal pipeline as much as possible. Since it is installed on a vertical pipeline, the effect of the liquid flowing upward or downward on the measurements is significant; upward flow may allow air bubbles to pass through and cause interference, while downward flow essentially makes proper measurement impossible. There is a problem with the installation location chosen for the flow meter.
Reply #52016-12-02
The poster can check the signal cable connectors and measure the supply voltage.
Reply #62016-12-03
The effectiveness of vortex flow meters depends greatly on installation and design calculations.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.