Thread Content
Class A and B pipelines are installed in utility tunnels; what are the required distances between such tunnels and buildings as well as roads? This is because Class A and B pipelines require a certain distance from buildings and roads.
There is a particularly detailed set of design specifications – I can’t remember exactly what they’re called; something like pipeline fire protection design specifications. Sorry, I haven’t looked at them in a long time
It should be included in GB50187; it’s probably in the appendix
Refer to the textbook for pressure pipeline reviewers
There are no requirements. None of the specifications have it.
The clear height and clear distances for pipe galleries are specified in GB50316-2000 (2008 edition), in Chapter 8
Articles 5.4.6 and 5.4.7 of GB50984-2014 specify this clearly.
5.4.6 The data in this table represent general requirements. 5.4.7 The minimum clear height specified in this clause takes into account two factors: one is the clear height requirements for the passage of railway locomotives, road vehicles, and pedestrians ; The second is pipeline safety. Due to the high safety requirements for pipelines carrying liquefied hydrocarbons, flammable liquids, and flammable gases, a minimum clear height of 6.0 m above the railway track top is specified, which is 0.5 m higher than the requirement set in the current standard \"Code for Fire Protection Design of Petrochemical Enterprises\" GB 50160.