Thread Content
For the regular tees that are commonly used, under what circumstances can socketed tees be used and under what circumstances cannot they be used? Does any expert know?
On pressure pipelines, do not use tees with directly cut openings.
Apart from pressure pipes, everything else should work, right? I can’t find any evidence
It can be used when the design specifications do not prohibit it. . . Including pressure pipelines, they can all be used. . Many people are terrified of it, mainly because the welding quality is inadequate; many people do not pay enough attention to the welding quality of these tees, which has led to numerous problems. .
GB 50316-2000 (2008 edition) Code for Design of Industrial Metal Piping
Strictly speaking, this is not called a socket tee; according to the standards, a tee cannot be referred to as such if there are no welds on the main pipes on either side of the branch pipe. It is called branch connection. When the ratio of the outer diameter to the wall thickness of the main pipe is greater than 100, the outer diameter of the branch pipe cannot exceed half that of the main pipe.
Article 12.3.12 of the \"Technical Code for Fire Water Supply and Fire Hydrant Systems\" (GB 50974-2014): When connecting the distribution main pipes (vertical pipes) to the distribution branch pipes (horizontal pipes), groove-type fittings shall be used; mechanical tees shall not be employed;
GB/T 20801.3-2020 5.1.7 Branch pipe connections and their fittings GB/T 20801.4-2020 7.8 Welded connections of branch pipes