As the title suggests, our system needs to be configured with a program that opens the valve when the liquid level is above 80% and closes it when the level is below 30%. I didn’t know how to create a group, so I found one in the program, copied it over and changed the tag numbers. But here’s the problem: this software is really unfriendly – it’s necessary to assign control stations first, and if there are points from two stations in the configuration, they can’t be displayed or outputted. How can this be fixed? I have connected the wires. http://bbs.hcbbs.com/forum.php?mod=image&aid=1296887&size=300x300&key=89f52833adc4977c&nocache=yes&type=fixnone
I’m not quite sure what you mean by that. First of all, copying it over is no problem. But the address needs to be reallocated and downloaded. There is also the card slot channel enablement. Just change the range again. There’s nothing else
We have several control stations, and during configuration it is necessary to assign stations; if it’s not the designated station, the data cannot be displayed or output.
We have several control stations, and during configuration it is necessary to assign stations; if it’s not the designated station, the data cannot be displayed or output.
With Emerson DCS, inputs and outputs must be under the same controller to be controlled. Cross-site is not possible. I’m not very familiar with Emerson DCS; we have a branch office that uses Emerson’s control system, so I have some basic knowledge of it. I’m not sure if this will be helpful to you