475: Debugging the Fisher locator – the display is incorrect

2018-03-24View Original

Thread Content

475: Debugging the Fisher locator; the actual opening is 45%, but the DCS shows 20%. What could be the reason? Does DCS need to be changed?
Reply #22018-03-24
Does 475 calibrate the valve stroke?
Reply #32018-03-24
Compare the current value shown in the 475 communication feedback with that of the ammeter on the serial port to see if they match
Reply #42018-03-24
Connect 475 and check what the feedback is. If it is 25, then check the locator (such as the original feedback value, parameter settings, etc.); if it is 45, then check the current, the wiring, DCS parameter settings, and so on.
Reply #52018-03-29
It seems this Fischer doesn’t have independent feedback.
Reply #62018-03-29
Model 6200 is available; the feedback is passive and requires connection to a 24V power supply

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.