24V electromagnetic flowmeter, without remote transmission, but it can have remote transmission by connecting a multimeter. What is the reason?
Reply #22018-09-18
There isn’t enough information in the problem description; check whether the correct setting is selected on the multimeter and whether the test leads are in good condition……
Reply #32018-09-18
It might be that the load isn’t sufficient; try using a 250-ohm resistor
Reply #42018-09-18
With the mA range in series, data is available on the DCS. No need to use a multimeter to connect the wires; there is no data from the DCS
Reply #52018-09-18
“Can you get remote transmission just by connecting a multimeter? It’s amazing! Damn old woman, it must be an electromagnetic flowmeter; its sexual instincts are starting to awaken, huh~~~ :P
Reply #62018-09-18
It’s just 2 small broken lines – other than the wires not being properly connected, what else could be the cause? :lol
Reply #72018-09-18
The current setting on a multimeter is equivalent to a wire; it’s impossible in theory. It’s likely that you haven’t connected the wires properly
Reply #82018-09-18
Is it a 4-20 milliampere output? Resistance only affects Hart communication; it has no impact on analog current signals, right?
Reply #92018-09-18
No remote transmission? Is that watch turned on?
Reply #102018-09-19
I’ve encountered that too; the reason is interference in the circuit. By adding an isolation barrier, everything works fine.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.