Process Engineering Division – Instrumentation and Automation Section – Daily Topics – Topic No. 2020-12-23: Discussion topic: 335. When using a single-flange level gauge to measure the liquid level in an open container, the distances from the gauge to the highest and lowest liquid levels are respectively h1 = 1 m and h2 = 3 m. If the density of the medium being measured is ρ=980 kg/m3, then: 2. If the height of the liquid surface is h=2.5 m, what will be the output of the electro-hydraulic level gauge? (5 points are given only to those who provide the correct answer; additional points are awarded for a correct calculation process or detailed explanation.)
Reply #22020-12-23
If the level gauge height H is 2.5 m, then (2.5–1)/(3–1) = 0.75; therefore, the output is 16 mA.
Reply #32020-12-23
A single-flange level gauge is used to measure the liquid level in an open container, with the distances from the gauge to the highest and lowest liquid levels being h1=1m and h2=3m, respectively. If the density of the medium being measured is ρ=980 kg/m3, then: 2. If the height of the liquid surface is h=2.5 m, what will be the output of the electro-liquid level gauge? Solution: I = (h – h1) / (h2 – h1) × (20 – 4) + 4 = (2.5 – 1) / (3 – 1) × 16 + 4 = 16(mA). Answer: The height of the liquid level is h=2.5m, and the output of the electro-liquid level gauge is 16mA.
Reply #42020-12-23
I=*(2.5-1)+4=16mA
Reply #52020-12-23
I=(h-h1)/(h2-h1)×(20-4)+4=(2.5-1)/(3-1)×16+4=16(mA).
Reply #62020-12-23
4+(2.5-1)/(3-1)*(20-4)=16ma
Reply #72020-12-23
If the level gauge height H is 2.5 m, then (2.5–1)/(3–1) = 0.75; therefore, the output is 16 mA.
Reply #82020-12-23
A single-flange level gauge is used to measure the liquid level in an open container, with the distances from the gauge to the highest and lowest liquid levels being h1=1m and h2=3m, respectively. If the density of the medium being measured is ρ=980 kg/m3, then: 2. If the height of the liquid surface is h=2.5 m, what will be the output of the electro-liquid level gauge? Solution: I = (h – h1) / (h2 – h1) × (20 – 4) + 4 = (2.5 – 1) / (3 – 1) × 16 + 4 = 16(mA). Answer: The height of the liquid level is h=2.5m, and the output of the electro-liquid level gauge is 16mA.
Reply #92020-12-23
A single-flange level gauge is used to measure the liquid level in an open container, with the distances from the gauge to the highest and lowest liquid levels being h1=1m and h2=3m, respectively. If the density of the medium being measured is ρ=980 kg/m3, then: 2. If the height of the liquid surface is h=2.5 m, what will be the output of the electro-liquid level gauge? Solution: I = (h – h1) / (h2 – h1) × (20 – 4) + 4 = (2.5 – 1) / (3 – 1) × 16 + 4 = 16(mA). Answer: The height of the liquid level is h=2.5m, and the output of the electro-liquid level gauge is 16mA.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.