Issues related to combustible gas controllers

2022-02-25View Original

Thread Content

Dear experts, may I ask if there are any requirements regarding the distance between combustible gas controllers and combustible gas detectors? There is currently a combustible gas controller located in the central control room, about 1 km away from the field detectors. Is this acceptable? If I use a computer cable to connect the signals, do I need to choose a cable with a cross-sectional area of 2.5 mm2?
Reply #22022-02-25
It doesn’t seem to have any requirements, but it’s so far away – will the information be okay?
Reply #32022-02-25
Is it out of fear of signal interference? Afraid it won’t be accurate
Reply #42022-02-26
It mainly comes down to the cables; cable resistance needs to be taken into account.
Reply #52022-02-28
Yes, 1000 meters with a cross-sectional area of 2.5 is sufficient.
Reply #62022-03-03
There are 2 solutions: 1. Use a fieldbus-based combustible and toxic gas controller, with the probes connected via a four-wire system; this setup can support distances of over 1 km. 2. The combustible and toxic gas controller is located in the on-site cabinet room of the device; signals are transmitted to the control room via fiber optics, where an upper-level computer is installed.
Reply #72022-03-04
A wire diameter of 1.5 should be fine; it’s better to use 2.5 if possible. For 4-20mA signals, a shielded control cable will suffice
Reply #82022-03-05
There are no specific requirements; as long as the signal transmission is fine, that’s enough
Reply #92022-03-05
1.5 is sufficient; most combustible and toxic substances operate at 24V. The main consideration is voltage drop, and using too thick cables results in high costs
Reply #102022-04-01
4~20ma, there is no need to worry about voltage drop for the signal.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.