Our company has manufactured two units for China’s Fifth Ring Road; their explosion-proof rating is as shown in the diagram above. Now we are required to carry out wiring work and use steel pipes for this purpose. If it is Zone 21, according to GB50058-2014, a control cable with a cross-sectional area of 2.5 square millimeters is required ; If it is Zone 22, only 1.5 square millimeters of control wire is required. It is currently in a state where the project has not been delivered. If the classification of explosion-proof areas was determined during the design phase, I can ask the people at China Five Rings ; If it needs to be determined before production, then the people at China Five Rings cannot yet decide whether this explosion-proof area is Zone 21 or Zone 22. I hope the experts here can help answer this.
The classification of explosion-proof areas is usually determined during the engineering design phase, which affects the safety standards and specifications for all subsequent equipment and piping designs. You can consult the relevant person in charge at Wuhuan or review the project design documents to confirm the specific division of explosion-proof areas. If not specified in the design document, it should be evaluated and classified by a qualified professional team. .
The classification of electrical explosion-proof areas is carried out by the electrical engineering department of the design institute; other departments such as those responsible for electrical systems and instruments can handle this task. The electrical and instrumentation equipment purchased must meet the explosion-proof requirements of the respective areas.