I have a question: what is the relationship between the volume of the circulating water tank, the cooling tower, and the amount of circulating water used?

2017-10-19View Original

Thread Content

I have a question for everyone: in a project where the water consumption for circulation is 500 m3/h, the cooling capacity of the cooling tower is 600 m3/h, yet the volume of the circulation tank is set at 100 m3. Could this meet the requirements? How to understand the consumption of circulating water? Does it refer to the water flow rate passing through a certain point each hour during the cycle? If the volume of the recirculation tank is 100 m3 and the water consumption for recirculation is 500 m3/h, then will the water overflow from the tank when the system is shut down and the water flows back? I’m a complete novice; I hope the more experienced members can help me resolve my doubts.
Reply #22017-10-19
The circulating water consumption is 500 m3/h, the cooling capacity of the cooling tower is 600 m3/h, yet the volume of the circulating water tank is set at 100 m3. It definitely cannot meet the needs.
Reply #32017-10-19
If the volume of the circulating water tank is 100 m3 and the consumption of circulating water is 500 m3/h, when the system is shut down the water flows back and overflows from the tank; there is no time to refill the water when the system is started up.
Reply #42017-10-19
There is also the issue of concentration ratio during operation; the volume of the circulating pool is 100 m3, so it is necessary to add water and remove wastewater frequently.
Reply #52017-10-19
The closed-loop theory is feasible, but when the system is stopped, water flows back and overflows from the tank; there’s no time to refill the water when the system is in operation, and water replenishment is often necessary
Reply #62017-10-20
The last edit to this post was made by *aol72 on 2017-10-20 at 08:16. No, it depends on the system volume; when the pump stops, the circulating water won’t flow back, unless the tank is at a lower level
Reply #72017-10-20
The last edit to this post was made by *aol72 on 2017-10-20 at 08:21. The capacity of the tank should be determined based on the capacity of the largest pump; when water is drawn directly from the tank, the volume should be at least equal to what that largest pump can deliver in 5 minutes
Reply #82017-10-20
Under normal circumstances, it is desirable for the system volume to be as small as possible, as this can reduce the amount of medication required
Reply #92017-10-20
The concentration ratio is related to the amount of evaporation and the volume of wastewater discharged; it is not related to the volume of the tank or the system. Please do not mislead others
Reply #102017-10-20
They know something, but don’t understand the specifics. Forgive them.
Reply #112017-10-21
The water consumption for circulation at 500 m3/h and the volume of the circulation tank at 100 m3 are two different concepts. It is not possible to calculate the increases and decreases simultaneously.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.