For two parallel circulation pumps, can the outlet check valve be removed?

2017-10-01View Original

Thread Content

Two 1000KW heat network circulation pumps operate in parallel, with hydraulic check valves installed at the outlets of each pump. I want to know if it’s possible to remove the check valves at the outlets of the two pumps.
Reply #22017-10-02
The purpose of installing a check valve is to prevent fluid from flowing in reverse, such as when a single pump stops operating or when pumps connected in parallel start or stop!
Reply #32017-10-04
No, in case one of them stops working, it will damage the pump
Reply #42017-10-05
No, it’s to prevent the pump from reversing; reverse rotation poses a risk of the locking nut coming loose as well as the impeller becoming detached
Reply #52017-10-07
It cannot be canceled. It can be installed on the main pipe.
Reply #62017-10-07
A check valve should be installed on the outlet pipe of each pump; it is not very useful to install one only on the main pipe.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.