The pH meter’s main display is not working properly

2015-07-14View Original

Thread Content

I have a pH meter here; sometimes the reading shown on the instrument at the site is normal, but the main control unit displays a value of 14. When I disconnect and reconnect the signal cable at the site, the problem goes away. What’s going on?
Reply #22015-07-14
A ammeter is connected in series within the circuit of the transmitter output; if the reading on the ammeter corresponds to the reading on the field instrument, it indicates that there is no problem with the field instrument, and in such cases the connection cables and the secondary sampling section should be checked. If there is no match, it indicates a problem with the output from the field instruments.
Reply #32015-07-14
At that time, the wire was removed to measure the current, and it was normal; after reconnecting the wire to the main controller, everything showed normal

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.