How to represent the signals from the distribution cabinet to the DCS in a PID diagram?

2015-11-05View Original

Thread Content

The signals from the variable frequency motor come from the power distribution cabinet to the DCS; I need to display these signals on the PID chart. How should I do that?
Reply #22015-11-08
Like the signals from other devices, it’s sufficient to show the signals that need to be drawn from the motor; in the PID display they appear to come from the motor, but in reality they originate from the power distribution cabinet
Reply #32015-11-08
For example, change the DCS instrument tag to SIC-001, and then direct the signal output to the motor.
Reply #42015-11-09
The signal from the DCS can only be sent to the frequency converter or the control terminal of the secondary circuit; it cannot be sent directly to the motor.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.