HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Fluctuations of the control valve

2016-04-03View Original

Thread Content

The eccentric rotary valve experiences regular fluctuations; a Messonier controller is used for it, and a pneumatic relay is added in between – could you please suggest a solution?
Reply #22016-04-04
1. The valve positioner is self-tuning; 2. There is a fault with the valve pressure reducing valve, which needs to be replaced; 3. The packing gland is tightened too much – loosen it a bit. These are the only reasons I can think of. We’ll need to analyze the specific issue further
Reply #32016-04-04
A problem with the valve positioner is highly likely.
Reply #42016-04-04
We’ve also encountered similar problems with the valves at Meiso; check the entire gas circuit, including the diaphragm head/cylinder section. If that doesn’t work, try replacing the positioner – we’ve replaced it twice
Reply #52016-04-05
The most likely causes are the locator, so try self-tuning; another possibility is air leakage from the air supply or fluctuations in air pressure – check those as well
Reply #62016-07-17
Check whether the actuator is leaking air, and check if the pressure relief valve is faulty. If the problem isn’t resolved, add me on WeChat at 26940238; I am from the manufacturer of Mersonilan products
Reply #72016-07-18
It’s likely the locator is self-tuning; perhaps the linear setting isn’t correct

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.