How far can an AI signal be transmitted using ZR-DJYJVP22 2x2x1.5mm2 cables? Can it reach 2000 meters?
Reply #22016-06-24
1000m should be no problem; I’ve never tried 2000m……
Reply #32016-06-24
I did the calculations; to achieve a voltage drop of 0.24V at 24V DC, 6 wires are required.
Reply #42016-06-24
24V minus the wire voltage drop should meet the power supply requirements of the on-site instruments (for example, 21.6V).
Reply #52016-06-24
I can’t even use it for 1000m. Too unreliable.
Reply #62016-06-24
Anyway, it’s not used within the requirements of national standards; to some extent, it exceeds those requirements. I recall there being national standards for the power cables of instruments – you might want to take a look at those. Today’s instruments are not that fragile; they can still function when the voltage drops to 22V. A rough calculation can be done for reference.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.