Emergency shutoff devices for hydrogen and chlorine pipelines in hydrochloric acid synthesis furnaces

2010-06-30View Original

Thread Content

This post was last edited by sunjl1981 on 2013-1-6 at 21:36. I would like to ask my friends: in the safety standardization inspection, there is a requirement to install emergency shut-off devices on the hydrogen and chlorine inlet pipelines of hydrochloric acid furnaces. What kind of devices are these? What is the purpose or function of installing them? I sincerely hope that knowledgeable friends can offer some guidance. # + + . hcbbs
Reply #22010-06-30
On-off valves are installed on the hydrogen and chlorine gas pipelines at the entrance of the synthesis furnace to quickly cut off the hydrogen and chlorine when the synthesis furnace is interlocked. It is mainly designed for safety.
Reply #32010-07-01
The main purpose of installing shut-off valves on the hydrogen and chlorine pipelines of the hydrogen chloride synthesis furnace is to promptly cut off these pipelines in the event of a fire or explosion at the furnace, thereby preventing such incidents from spreading to the chlor-alkali system.
Reply #42010-07-01
It’s chlorine gas, as well as hydrogen gas in the pipelines, along with shut-off valves to prevent safety issues resulting from emergency shutdowns or other accidents
Reply #52010-07-01
It’s chlorine gas, as well as hydrogen gas in the pipelines, along with shut-off valves to prevent safety issues resulting from emergency shutdowns or other accidents
Reply #62010-07-02
I’d like to ask the fellow maritime professionals upstairs again: for the shut-off valve, a interlock mechanism is required. Is it better to use a pneumatic valve or a solenoid valve? What are the cascade control parameters you’re using?
Reply #72011-12-31
The pneumatic valves used in our company have a too long stroke time; solenoid valves are better

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.