By replying with bg9.png, you can see the answer to the previous question (a calculation problem). There is a double-flange level gauge transmitter for a storage tank; the lower flange of the level gauge corresponds to the lower limit of the liquid level. The distance between this lower flange and another point is h1 = 0.5 m, as shown in the diagram. The density of the liquid being measured is ρ1 = 960 kg/m3, and the distance between the centers of the upper and lower flanges is h2 = 5 m. The calibration range of the level gauge is from -47 kPa to -3.8 kPa. Due to damage to the diaphragm, a new double-flange level gauge needs to be installed. The density of the filling fluid in the capillaries of this new gauge is ρ3 = 1060 kg/m3. What is the calibration range of the level transmitter after the replacement? (g=10m/s2) The answer is: -53kPa to -9.8kPa. (The question for this round is as follows: Multiple-choice question) A differential pressure flow meter used in the field, with a range of 40kPa and a maximum flow rate of 16t/h. When the differential pressure is 10kPa, what is the output current of the transmitter and the corresponding flow rate? A. 12mA, 8t/h B. 8mA, 4t/h C. 8mA, 8t/h D. 12mA, 12t/h —————————————————————————————————————————————————————————————— Scoring criteria: Incorrect answers earn 2 wealth points; *incomplete* answers earn 3–6 points. Correct answers with detailed explanations, along with supplementary *answers*, earn 10–15 wealth points. Please score according to these criteria. Note: If there are editing records after answering, only those who participated will be credited points. For continuous malicious spamming, 2 points will be deducted each time, with no upper limit. Pure numbers, pure emojis, or random letters unrelated to the answer are all considered malicious spamming; points will start to be deducted after three warnings
Reply #22017-09-14
A differential pressure flow meter that performs on-site calculation, with a range of 40 kPa; the corresponding maximum flow rate is 16 t/h. When the differential pressure is 10 kPa, the output current of the transmitter and the corresponding flow rate are ( A ) A. 12 mA, 8 t/h B. 8 mA, 4 t/h C. 8 mA, 8 t/h D. 12 mA, 12 t/h
Reply #32017-09-14
A、12mA 8t/h: A differential pressure flow meter with on-site calibration, having a range of 40kPa; the corresponding maximum flow rate is 16t/h. When the differential pressure is 10kPa, the output current of the transmitter and the corresponding flow rate are (A、12mA 8t/h). A、12mA 8t/h B、8mA 4t/h C、8mA 8t/h D、12mA 12t/h

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.