The signal of the differential pressure transmitter fluctuates greatly

2018-03-06View Original

Thread Content

Differential pressure transmitters are used to measure the differential pressure between indoor and outdoor areas; the positive-pressure side is installed indoors, while the negative-pressure side is in direct contact with the outdoor atmosphere. Wind forces can cause fluctuations in the pressure signal. I was wondering if any experts have any good solutions, perhaps ones that can be implemented using the instruments themselves. Maintain a negative pressure of 60 Pa indoors and outdoors
Reply #22018-03-06
This post was last edited by 1111111 on 2018-3-6 at 19:39. So it’s indeed the wind causing unstable measurement values; that’s easy to fix. . . The fear is that the micro-differential pressure gauge you’re using has a large time drift and can’t maintain stability…… I can’t even remember how many people’s gauges I’ve had to fix already. Which brand’s watch are you using, and what’s the model? Tell me so I can hear about it; it would be better if you could take a photo and post it. I’ll assess its condition and teach you how to check whether it’s stable or not first. Separator line-------------- Additionally, the micromanometers manufactured by Gozao, models SC322 or SC329, feature self-calibration without zero drift; they are highly sensitive yet extremely stable. For your reference, there are images to prove it – 1 hPa = 100 Pa = 0.1 kPa.
Reply #32018-03-06
The poster can take windproof measures for the outdoor negative-pressure chamber
Reply #42018-03-06
It’s rather troublesome to lead the pressure measurement pipeline to a space unaffected by wind
Reply #52018-03-06
It’s from the Rosemount 3051 series, model number 3051CD02A01A; there’s another sequence of numbers at the end which I can’t remember. Is this information enough?
Reply #62018-03-06
A protective cover was installed, but it didn’t work well; there are still significant fluctuations when the wind is strong. I’m not sure if the cover isn’t large enough
Reply #72018-03-06
How many bends are there in the pressure sampling pipeline of the positive pressure chamber?
Reply #82018-03-06
“Is the model number 3051CD02A01A”? It’s a sample from the experts; I haven’t seen it in over 10 years. I can’t figure out the range of values for this code. Please just tell me directly. You measure 60 Pa, which is negligible, while the 3051 model, with a full tank of oil, has plenty of capacity – it has a measurement range of around 60 Pa; shall I give that to you? .
Reply #92018-03-06
Dude, that’s a micro-differential pressure transmitter – a single puff of air can knock it over. So just add an instrument enclosure and place the transmitter inside it; that’s what we do! :lol

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.