Pressure guiding pipeline for instruments used to measure liquid oxygen or liquid nitrogen (-196°C)

2018-08-02View Original

Thread Content

Is it required by design to have a thermal insulation layer for the pressure guiding pipelines of instruments used to measure liquid oxygen or liquid nitrogen (-196°C)?
Reply #22018-08-02
With low-temperature pressure measurement, if the pressure transfer lines are insulated, then the pressure measuring instruments will freeze up in no time at all :lol.
Reply #32018-08-02
It cannot maintain coldness; the reason is the same as that for measuring steam – a cooling section must be provided – and the same applies when measuring cryogenic fluids, as a cooling section is necessary.
Reply #42018-08-02
No, liquid nitrogen vaporizes as soon as it enters the instrument pressure guide tube, causing the pressure guide tube to reach near ambient temperature.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.