Address conversion for master-slave communication between TRICON and PKS via MODBUS

2020-10-23View Original

Thread Content

MODBUS communication is used with TRICON and PKS, with PKS acting as the master station to read from and write to TRICON. TRICON has defined an AI: r1201FZT_111102A, also known as 33028; it is a 32-bit memory-based real number. When reading via MODBUS and creating points in QUICK BUILDER on the PKS side, why is the communication address 35055? How is this value determined? I would appreciate the advice from all the experts
Reply #22020-10-23
The result should be 33028 – 30000 = 3028; 3028 * 2 – 1001 = 5055; 30000 + 5055 = 35055
Reply #32020-10-23
Why is this the case? Are there any relevant materials?
Reply #42020-10-27
If reading the real-valued data in tricon, the calculation must be done using the algorithm mentioned above; if it is an integer value, simply use the address directly

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.