Process Engineering Division – Instrumentation and Automation Section – Daily Topics – Topic No. 2021-01-25

2021-01-25View Original

Thread Content

Process Engineering Division – Instrumentation and Automation Section – Daily Topics – Topic No. 2021-01-25: Discussion question: 368. What impact will minor leakage in the balance valve of a orifice flow meter have on the flow measurement results? What’s the reason?
Reply #22021-01-25
If the balance valve of the orifice flow meter leaks slightly, the measurement results will be lower than accurate. Because micro-leakage causes the pressure difference across the orifice plate to decrease.
Reply #32021-01-25
If the balance valve of the orifice flow meter leaks slightly, the measurement results will be lower than accurate. Because micro-leakage causes the pressure difference across the orifice plate to decrease
Reply #42021-01-25
If the balance valve of a orifice plate flow meter leaks slightly, the measurement results will be on the low side. Because micro-leakage causes the pressure difference across the orifice plate to decrease.
Reply #52021-01-25
The measurement result is low; internal leakage in the balance valve causes a decrease in pressure difference
Reply #62021-01-25
The slight leakage in the balance valve reduces the pressure difference between the positive and negative pressure sides, resulting in a lower reading
Reply #72021-01-25
A slight leak in the balance valve can cause the measured differential pressure to be low, resulting in an underestimation of the flow rate; the flow measurement is particularly inaccurate at low flow rates.
Reply #82021-01-25
The measured value will be on the low side. There is a slight leak in the catheter on the positive pressure side, so the measured positive pressure value is slightly lower
Reply #92021-01-25
A slight leak in the balance valve of a orifice plate flow meter results in lower flow measurement values, as the slight leak causes the differential pressure across the transmitter to decrease, thereby reducing the flow rate
Reply #102021-01-25
A slight leak in the balance valve reduces the pressure difference between the positive and negative sides, resulting in a lower reading on the instrument.
Reply #112021-01-25
If the balance valve of a orifice plate flow meter leaks slightly, the measurement results will be on the low side. Because micro-leakage causes the pressure difference across the orifice plate to decrease.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.