AO output issue in CENTUM VP

2021-06-16View Original

Thread Content

I have a question: I want a certain valve to be controlled at 50-100%, and can the output range be 12-20mA instead of 4-20mA? Is it possible to achieve this in this way?
Reply #22021-06-16
If it is kept between 50% and 100%, doesn’t that correspond exactly to 12–20 mA?
Reply #32021-06-17
This post was last edited by qugd on 2021-6-17 at 12:14. I recall there being signal conversion modules with arithmetic functions that can take a default 4–20mA signal and, through configuration, convert it into other output formats; something like translating the signal on a coordinate axis or converting it using a DCS – that should be possible
Reply #42021-06-17
Yes, stepwise adjustment provides this type of output
Reply #52021-06-18
It’s simply output limiting; both DCS and PLC can achieve this

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.