In level gauges, what are the respective functions of 4-20mA and 485? What’s the difference from HART?

2021-05-31View Original

Thread Content

In level gauges, what are the respective functions of 4-20mA and 485? What’s the difference from HART?
Reply #22021-05-31
These two things have nothing to do with each other; 4-20MA transmits a standard current signal, while 485 is a communication protocol.
Reply #32021-05-31
It seems the poster has also just started working with instruments
Reply #42021-05-31
Well, do you mean that too? Are you the same? ;P
Reply #52021-05-31
What is the method of communication? Seeking advice from an expert: handshake
Reply #62021-05-31
Find some information to look at; there’s too much text to explain everything at once
Reply #72021-06-02
4-20mA: Analog signal; 485: Digital signal, typically using the MODBUS protocol; HART: Digital signal, a type of communication protocol. It is generally used in combination with 4-20mA.
Reply #82021-06-02
I’ve learned it: handshake. One more question: what are the different functions of each of them?
Reply #92021-06-02
4-20mA can transmit the meter’s measurement value as an analog signal to a secondary instrument or control system; generally, only the measurement value is transmitted; RS485 generally uses the MODBUS protocol to transmit the meter’s measurement values, status, alarms, etc. in digital form to the MODBUS master station ; The HART protocol is typically used in conjunction with 4-20mA signals; it is possible to configure the instrument using a handheld programmer, and control systems that support HART can detect whether there are any faults with the instrument. Simply put, it means that the measurement values are transmitted via 4-20mA ; MODBUS can transmit the alarm values and fault status of level gauges, etc ; The HART protocol allows the handheld communicator to set parameters such as the measurement range of the instrument. Control systems generally receive 4-20mA signals, corresponding to the set physical range.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.