If a gauge, flow meter, uses 485 communication and works fine in the office but not on site, what could be the reasons?

2021-02-10View Original

Thread Content

This post was last edited by conde on 2021-2-10 16:51. If a meter, flow meter, uses 485 communication, works fine in the office but not on site with no communication, what could be the reasons? It’s a turbine flowmeter. Communication works fine using the MODSCAN software, but when sending them to customers, half of the units fail to communicate. However, when those units that communicate properly are connected to the faulty lines, communication works again. What could be the reason? I just received feedback from the customers and I can’t think of any possible causes. An engineer will be sent over after the New Year
Reply #22021-02-10
First, ensure that the laptop you carry with you is a device that functions properly for communication; use it to replace the customer’s computer in order to establish a connection. If communication is possible with this laptop, it indicates that the serial port on the customer’s computer may be damaged or faulty. It’s happened here too – it really gave those engineers a tough time
Reply #32021-02-14
It’s very likely to be a wiring issue; for 485 communication, certain requirements exist regarding the wiring when the distance between the devices is large
Reply #42021-02-15
The computer is working fine, but the gauge at the site was malfunctioning; after replacing it with another gauge, everything worked properly again
Reply #52021-02-15
The computer is working fine, but the gauge at the site was malfunctioning; after replacing it with another gauge, everything worked properly again
Reply #62021-02-16
It’s most likely a problem with the instrument. Try reducing the baud rate if the instrument is not working properly.
Reply #72021-02-19
Waiting for the moment when the truth emerges. . . .
Reply #82021-02-20
Consider the following points: 1. The communication distance is too long. 2. There is interference. 3. Connect in series, not in star configuration. 4. Add a reflection resistor.
Reply #92021-02-24
It’s fixed now; one of the small resistors was changed. I’m not sure what it was, but it is said that this increased the driving power for the 485 interface
Reply #102021-02-25
Terminal 120 ohm reflection resistance

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.