HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

PID diagram analysis

2024-01-20View Original

Thread Content

1. May I ask the experts, what do GT, GSH, and GSL stand for respectively? Thank you for the reply.
Reply #22024-01-20
Also, for interlock C 14 in the diagram, where can I find its description? Thank you
Reply #32024-01-21
GT refers to the valve positioner, while GSH and GSL are the open and closed limit switches respectively
Reply #42024-01-21
Thank you for your reply. Aren’t the responses usually from ZSO and ZSC? There’s also the whole H, L. . . . . .
Reply #52024-01-22
A gas detector transmitter is generally denoted by GT. GSH and GSL represent high and low alarms. Take a look at the legend of the flowchart to see if there are any annotations or other detailed data tables. It might detect leaks.
Reply #62024-01-22
GT Our factory indicates gas detectors
Reply #72024-01-23
G gas detection, S series, H high, L low, T transmitter
Reply #82024-01-23
This should be a safety instrument interlock; check I/10
Reply #92024-01-27
C14 is triggered by ESD, and ESD refers to an emergency shutdown; usually, this occurs when the emergency shutdown button is pressed

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.