Seeking help with instrument migration issue

2009-12-31View Original

Thread Content

We generally talk about moving transmitters using ideas – how exactly is this done? Could you give an example to illustrate it? Thank you
Reply #22010-01-06
Migration is carried out using a handheld communicator; in simple terms, here is the corresponding relationship for range migration: if the instrument’s original range is 0–40 kPa, then 4 mA corresponds to 0 kPa, and 20 mA corresponds to 20 kPa. If you want to display the range of -20–20 kPa, you simply need to set 4 mA to correspond to -20 kPa and 20 mA to correspond to 20 kPa

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.