2016-08-02View Original

Thread Content

Have any seniors used the AOP panel with Siemens 440 frequency converters? I currently want to copy the parameters from frequency converter A to frequency converter B using the AOP panel. The upload of parameters from frequency converter A to the AOP panel was successful, but when attempting to download those parameters to frequency converter B using the AOP panel, the corresponding parameter sets could not be found. What could be the reasons for this situation?
Reply #22016-08-04
Siemens has parameter groups, which must be set in order to view the corresponding parameters
Reply #32016-08-04
Try setting P0003=3
Reply #42016-08-04
This post was last edited by Han Cheng (Zi Xiang) on 2016-8-4 at 16:45 :Q so awesome

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.